Hydro Flame 8012 Humming
Discussion in 'Heating / Cooling Systems' started by Bamabrat, Feb 11, 2019.
  1. ashtonc77
    ashtonc77 New Member
    Jan 17, 2019
    If I remember correctly, the process for the heater to start is that when the air temp goes below the thermostat set temperature, it connects the 2 wires together (hence the reason you can just connect the 2 wires together without the thermostat) which sends a signal to the heater telling it to start. After a few seconds (probably 5 on yours), the heater fan should then start. 30 seconds after that, the heater should light.
    Based on this assumption and the information you provided, it sounds to me like the wires to your thermostat are working properly and sending a signal to start the fan. When the fan goes to start up it sounds like it is drawing more current then is expected hence the reason your lights are dimming and the breaker is tripping. I would check the wiring to the fan and verify that it is wired correctly and make sure there are no loose wires floating around which could be making contact with another conductor and causing problems. You could also get a 12 volt battery and connect it directly to the fan to make sure the fan is operating correctly (turns on and spins). There is a slight chance that there is a problem with the fan motor and it is drawing more current then expected. It could still be a problem with the control board which might not be possible for you to diagnose.
  2. Sjm9911
    3,294
    1,537
    Short somwwhere as stated, only way the breaker would trip. Fan is a good suspect.
  3. theseus
    theseus Centerville, OH
    2,758
    362
    Feb 6, 2007
    Centerville, OH
    Everything in the furnace is DC power. Breakers don’t trip over DC power. Fuses blow though.
    I feel it necessary to point out that not all old furnaces auto light. My 86 Coleman Columbia had a pilot light in the furnace.
  4. Sjm9911
    3,294
    1,537
    Yes fuses not breakers, his first post had pictures, in them was the direct spark ignition.
  5. theseus
    2,758
    362
    Feb 6, 2007
    Centerville, OH
    Excellent! Carry on then...:)
  6. WrkrBee
    WrkrBee Well-Known Member
    1,718
    627
    I do not have this furnace and basically doing a seat of the pants flyover. I'm trying to learn something, too. If the 12v fan starts first, and that's when the lights dim, best guess there is a fan wire shorted between the control board and the fan or the control board has a short on it.
  7. theseus
    2,758
    362
    Feb 6, 2007
    Centerville, OH
    Im guessing, given that the lights are dimming that the converter is maxed out and might be at the end of its life...
  8. BillyMc
    BillyMc Well-Known Member
    621
    252
    Mar 25, 2018
    If it's humming and there is no air blowing you probably have a problem with the blower motor. You need a 12v power source (battery or converter) for the furnace to work.
    Some furnaces do have 12v DC circuit breakers (mine has a 5amp). There are also manual and auto reset breakers to replace the other fuses in your PUP.